Seismic load combination

Status
Not open for further replies.

SHBH

Structural
Joined
Mar 23, 2007
Messages
55
Location
GB
Hi,
I was checking cl 12.4.2.3 for seismic load combinations, in which 0.2Sds is used to account for the seismic load in vertical direction. For rest of the horizontal seismic loads , one can use 100% in X dir and 30% in Z dir (seismic design cat D).
What if 100% is in the vertical direction, should it then be 100%Vertical + 30% hor-X + 30%hor-Z
I have seen this combination to be used in some other design offices, but where is the ref in code.

 
100% Vert + 30%X + 30%Z?? No.

The primary seismic is always either X or Z. The vertical is just an added seismic effect that accompanies the X or Z.

 
I've seen something like this before and I think it could possibly have come from ASCE 4 for "Seismic Analysis of Safety-Related Nuclear Structures" although I can't find it in the spec now. It might have been in other contract specs.

Regards,
-Mike
 
Thanks JAE & Mikee,
From this discussion now i can remember that the 100% vertical seismic effect was really mentioned in the nuclear DBR.
so the eccence is vertical has to be 20% if i am using ASCE7 load comb.
 