bsmet95 (Mechanical) said:
A customer has a rather unusual request for some calculations. Our track is to be installed in a building in a seismic zone, and in case of seismic activity he wants the track to fail before the building does. According to ANSI spec's., each span of the track is to be considered a simple beam.......
It is hard to estimate the probability that the earthquake will occur when the monorail /overhead crane is loaded..However, The LL suspended to monorail will not vibrate together with the building structure. But, monorail beam and travelling trolley will vibrate , that is the beam wt and trolley wt with crane should be added to seismic wt.
I have designed acc. to various codes in past and remember that ,only Russian Code SNIP includes the LL for monorails or overhead cranes for only VERTICAL SEISMIC EFFECTS..
I will say with using engineering judgement, the weight increase (in the range of %30 ) due to seismic event will not cause the lateral buckling of the monorail beam..
ASCE 7 'C12.7.2 Effective Seismic Weight. During an earthquake, the structure accelerates laterally, and these accelerations of the structural mass produce inertial forces. These inertial forces, accumulated over the height of the structure, produce the seismic base shear. When a building vibrates during an earthquake, only that portion of the mass or weight that is physically tied to the structure needs to be considered as effective. Hence, live loads (e.g., loose furniture, loose equipment, and human occupants) need not be included. However, certain types of live loads, such as storage loads, may develop inertial forces, particularly where they are densely packed. Also considered as contributing to effective seismic weight are the following:
1. All permanent equipment (e.g., air conditioners, elevator equipment, and mechanical systems);
2. Partitions to be erected or rearranged as specified in Section 4.3.2 (greater of actual partition weight and
10 lb∕ft2 (0.5 kN∕m2) of floor area);
3. 20% of significant snow load, pf > 30 lb∕ft2 (pf > 1.4 kN∕m2) and
4. The weight of landscaping and similar materials.