Here's the situation:
Wood framed building
Wood shear walls using proprietary hold downs.
Hold downs using cast-in or post-installed hold down anchor bolts
Design of the bolts per Appendix D of ACI 318
Bolts extending into a continuous trenched concrete footing.
Question:
Would the embedded bolts be considered to be in a "Cracked" concrete section or an "uncracked" concrete section? This makes a huge difference in load capacity.
Previous assumptions:
I always thought that the cracked condition was typically for the bottom of flexural beams with the concrete in tension. For a footing, the top of the footing isn't in tension - except in a seismic event, the footing may be uplifted by the shear wall and the deformed shape of the footing implies a tensile condition near the hold down anchor bolt.
Also - if the answer is to simply check to see if there is net uplift on the footing at the hold down - do you use an R = 1? Or do you use the R for the shear wall system?
Do you use 0.6D + .7E? Or the ACTUAL condition of D + .7E. Or do you use D + 1.0E?
Wood framed building
Wood shear walls using proprietary hold downs.
Hold downs using cast-in or post-installed hold down anchor bolts
Design of the bolts per Appendix D of ACI 318
Bolts extending into a continuous trenched concrete footing.
Question:
Would the embedded bolts be considered to be in a "Cracked" concrete section or an "uncracked" concrete section? This makes a huge difference in load capacity.
Previous assumptions:
I always thought that the cracked condition was typically for the bottom of flexural beams with the concrete in tension. For a footing, the top of the footing isn't in tension - except in a seismic event, the footing may be uplifted by the shear wall and the deformed shape of the footing implies a tensile condition near the hold down anchor bolt.
Also - if the answer is to simply check to see if there is net uplift on the footing at the hold down - do you use an R = 1? Or do you use the R for the shear wall system?
Do you use 0.6D + .7E? Or the ACTUAL condition of D + .7E. Or do you use D + 1.0E?