Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

SCBF

Status
Not open for further replies.

Ducla

Structural
Dec 18, 2012
1
I am designing a one story SCBF with a zipper column to resist unbalanced loads. Is there something in the code that says I don't need to design the pad footing under the zipper column for the material overstrength of the capacity of the braces? The footing would be very large if I have to design for this unbalanced load.
 
Replies continue below

Recommended for you

"If the foundation is allowed to uplift
or rock, as might occur in shallow foundations, then
the foundation only needs to develop the weight
associated with the foundation (spread footing, grade
beams, slab-on-grade, soil wedge along side of
footing, etc). A factor of safety should also be
considered regarding the calculated foundation mass
since you may not be accounting for all mass present.
The author recommends a 1.3 factor of safety
multiplier on the calculated mass since it is hard to
predict precisely how the foundation will behave.
If the foundation is considered fixed, or not subject
to uplift movement (pile foundation or large
subterranean structure) then the brace tensile yield
vertical component needs to be developed into the
foundation
."
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor