Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

SCBF - Magnified moments and Maximum force delivered

Status
Not open for further replies.

OUe

Structural
Joined
Feb 14, 2007
Messages
47
Location
US
I'm trying to design my columns for SCBF's and I was wondering if I need to use the combined loading effects of chapter H utilizing the Pmax determined by the RyFyAg of the brace. I have an inverted V-type brace at the roof level, which yields a huge beam at the roof level. The AISC 341-02 provisions allowed an exception to any roof-level (or penthouse) beams. Because this provision is now out of the 341-05 code, I have to design it for a braced system utilizing the capacity of the brace. The force due to the brace is so much larger than the uniform loading on the beam that I am forced to size a smaller brace so that my beams aren't over 300 plf. AISC 341-05 allows an exception on the brace-size as long as the maximum force is delivered to the column from the bracing system. Therefore, when I use Pu/phiPn + 8/9(...), should I use Pmax(from the brace)/phiPn in this equation? Any comments would be appreciated.