What if the terminals go to the wrong phase or are connected in the wrong polarity? The saturation test will not show this.BUT if the terminals do NOT go to your CT's, you won't replicate your previous figures.
So, are you certain that the things connected to these multiple connections can withstand the voltage of a saturation test?but in between the CT at the circuit breaker and the relay or meter, there are multiple connections.
Actually, it will. The winding acts like an autotransformer. This is the reason that you can't use part of the winding in high impedance differential ralays unless you carefully evaluate the full winding voltage.I question your assertion that performing an excitation test on lower ratios of multi-ratio CTs will impose a higher voltage over the full winding.
were actually true then an open circuited CT would be quite benign as there is no current flow. You and I both know that an open circuited CT is far from benign.then the voltage measured from X1-X5 would also be 400V, because there would be no current flow between the X3 and X5 terminals