bigAlittlee
So I am doing some retro-commissioning work on an older building that currently wets all 4 cooling tower cells at all times. Control valves do not exist. Single speed fans are sequenced by thermostats in each basin, each of which control their respective fan to operate at varying basin temperatures. For example at basin temp = 70F fan 1 runs, at 72F fans 1 and 2 run, at 74F fans 1, 2 and 3 run, and at 76F all 4 fans run.
Obviously there are improvements to be made to the current sequence of operation, and VFDs for the fan motors will be installed before cooling season, which will help a lot.
Engineers have made comments about running cooling towers "too dry" and by too dry in this case, that means 25% of design water flow. The majority of the time a single pump of 4 (matched to the 4 towers) is ran, over 4 towers, so they run at 25% flow each. One concern with running too dry, that I understand and agree with, is that when fill is dry, it is more prone to the accumulation of scaling, but in this case the water quality is very well maintained so I don't see this as a problem. I don't see any other issues.
Basically I see two options:
1. Continue to circulate over all 4 cells in all circumstances, but change fan control to stage fans simultaneously and adjust speed to maintain a 7F approach. With 4 cells there is more heat transfer area, and I would expect this equates to a lower ratio of fan power to heat rejected.
2. Define a minimum tower flow, add control valves for each tower, and sequence towers in a way to ensure that this minimum flow is maintained.
I think option 1 is the favored option. Does anyone disagree? Thanks.