We have a client that wants to add a generator to a roof of an industrial building that has metal decking and 32LH07 bar joists feeding to an interior 40G 6N 12k girder joist. The generator is a 2600lb unit of 42"x94" base (92psf). My question for those that may do these more often than us, when analyzing the existing joists (we have erection drawings) how do you typically handle the load combinations with an RTU? It should fall under the roof live load criteria, but do you include the design roof live load on the existing plans (20psf) over the entire area and also add the concentrated load in the area of the RTU? In our area the snow load is the same as the roof live load, 20psf.
Any concerns with placing the generator centered over the interior 40G girder joist near the support? My thought is the load of the generator would have four contact points, one on each 32LH joist that connects to the 40G, as well as two contact points on the 40G. This would minimize the concentrated loads on the top webs compared to centering it over a single 32LH joist. This assumes the joist can handle the shear loads as well as the bearing on the precast tilt up wall panels, which we would check. Another option is centering it between two 32LH joists and add angles to transfer the loads to the joists (joists @ 6'-8"cts and generator is 3'-4"). Attached is a roof framing plan in case it helps. The client wants to keep it away from the 2nd floor area (to the right in the plan), but the electrical boards are all located under the 2nd floor area at ground floor. One option was to put the generator towards the wall at the far left, but then you have a long run of electrical wire to the boards. Thoughts?
The Lennox weighs 2570lb, the Carrier weighs 755lb, and the Cook vent fan is unknown at this point but definitely less than 500lb.
Any concerns with placing the generator centered over the interior 40G girder joist near the support? My thought is the load of the generator would have four contact points, one on each 32LH joist that connects to the 40G, as well as two contact points on the 40G. This would minimize the concentrated loads on the top webs compared to centering it over a single 32LH joist. This assumes the joist can handle the shear loads as well as the bearing on the precast tilt up wall panels, which we would check. Another option is centering it between two 32LH joists and add angles to transfer the loads to the joists (joists @ 6'-8"cts and generator is 3'-4"). Attached is a roof framing plan in case it helps. The client wants to keep it away from the 2nd floor area (to the right in the plan), but the electrical boards are all located under the 2nd floor area at ground floor. One option was to put the generator towards the wall at the far left, but then you have a long run of electrical wire to the boards. Thoughts?
The Lennox weighs 2570lb, the Carrier weighs 755lb, and the Cook vent fan is unknown at this point but definitely less than 500lb.