Doug,
We are interested in determining if there is porosity or broken rotor bars in the cage. Currently we run the motor on a dyno to be able to load test to 1.0 SF or better. This is all part of troubleshooting if a bad rotor is suspected. On larger motors, the cost to run the motor under load is expensive. We would like to be able to test the rotor cage integrity without loading the motor, thus reducing our testing cost. Current analysis is performed at the present time and we look for sidebands around 60 hz at +/- slip. Evaluate based on the delta dB of 45 db or less to determine the presence of bad rotor bars. So far, correlation has been verified with visual inspection after teardown. We've also seen some correlations between single phase testing and current analysis. If it fails single phase test, it fails current analysis. However, if it passes single phase, it still may not pass current analysis. So single phase testing is not a catch all. Any information you can lend is appreciated. Thanks.