Triangled - here is my attempt but I believe it wasn't kept too simple:
[blue]Dear Mr. Client:
You have requested information regarding snow loading of the roof of your building located at 123 Main Street, Anytown, USA. As you are aware, our firm designed your roof system for you recently based upon the applicable building code for the city. That code references snow load requirements which, for this area requires a minimum uniform roof snow loading of 36 lbs. per square foot.
Your request was to understand the types of situations where occasional, higher snow loads may occur that would necessitate snow removal to avoid damage or collapse of your roof structure.
In general, the design snow load of 36 psf, based upon the code, relates to an average depth of 1.8 feet (22 inches) of snow.
However, please allow us to point out several concerns with relying on this simple depth:
Density Issues
The density of snow that accumulates on the roof can vary significantly. Multiple snowfalls in several days or weeks can create snow densities much higher, and result in a lower depth of snow with the same design loading. Thus, a 22 inch snow depth may actually be higher or lower than the design load.
Drifting Issues
Snow may accumulate near roof irregularities causing drifting and wild variations in the snow depth. Knowing where and how to measure non-uniform snow depths and how they relate to our design load can be difficult. And excessive drifting could create possible structural concerns in smaller, localized areas. Our design included code required loading for the irregularities included in the design as the building is currently configured.
Water Ponding
Snow can be partially melted in sequential warm days causing significant amounts of water to pond on the roof, especially when snow and ice block or clog drains or scuppers. This can cause serious problems with the accumulation of water on the roof, creating large loads in low or depressed areas of the roof.
Changes in the roof structure
Over time, there may be variations in other types of loads on our roof that could affect how snow loading affects your roof. In the future, additional roof top units, heavier roofing, or equipment hung from the roof inside the building can alter the amount of snow that the roof can support.
So relying on a single snow depth that would trigger action on your part to begin removal operations may not be correct for any given snow or building condition and this might cause you significant unneeded expense if the density is really lighter than assumed, or create an unsafe condition if the density is heavier than assumed.
To at least offer you a general idea or range of values that is possible, consider that snow density can vary between 15 lbs/cu. foot and 30 lbs./cu. foot. This would create a range of depth values for your roof of:
Low depth: 14”
High depth: 29”
These values are based upon our safe maximum load which includes a safety factor. If we remove the safety factor from the depths above we would have the following range of depths that would approach, or equal the theoretical collapse load:
Low depth: 22”
High depth: 46”
From this you can see that due to variations of density the maximum critical depth is not easy to rely on, but hopefully this provides you with at least some understanding of what you have.
Our recommendation would be to not rely on a simple depth measurement. Instead we would recommend that you monitor any situations which would warrant special attention and prompt further investigation. These would include:
1. Significant snowfalls in the higher ranges listed above
2. Snowfalls on sequential period which follow one another prior to the early snowfalls melting away.
3. Rain-on-snow conditions.
4. Significant snow storms noted as historical or above average.
5. Changes in equipment, units, penthouses, screens, etc. that are newly placed on the roof.
6. Changes in equipment or elements newly hung from the roof inside.
7. Changes in roof framing such as sagging, water ponding, or leakage.
8. Any evidence of drains blocked.
If those conditions should occur, we would be happy to assist you in further looking at your roof and how those conditions might affect its structural performance.
Sincerely,
ABC Structural Engineering, Inc.
John Doe, P.E.
Engineer At Large
[/blue]
faq731-376