I'm one of the first to say post a sketch, so if this is the case with this question let me have it...
New Building:
Wind but no seismic, in Florida
35ft tall tilt panels including parapet, roof height @ 30ft/
Steel framing interior, front side only will have offices with a second floor (steel frame and composite deck-slab) and the rest is open light industrial and warehouse.
I have selected two locations at plan geometry changes for expansion joints in the roof, and because the length of the roof requires them, dividing the roof into 3 sections. For the purposes of this discussion it can be one long rectangle with an approximate 4:1 ratio for the whole building.
1. Forgive me if this is a silly question, do I need to continue the expansion joint at the second floor also? I only have a second floor along the front side of the building that extends back about 1/4 of the building width.
My immediate response is no, the expansion joint is for the roof not the entire building. Worse case I have only 3/4" of total expansion at each joint, which includes the end and center sections.
The expansion joint(s) detail right now is along a single column line with one roof WF beam. This beam will also act as a drag strut and at one end of the building as part of a braced frame.
Both sides of the deck are mounted to two continuous plates that can slide on top of the WF with a gap in between obviously to accommodate the movement. I assume I need to let both sides of the roof float.
2. BUT- Can I rigidly connect the middle roof section along both edges and design for expansion while allowing the end sections to slide at the expansion joint? Or must both sides of an expansion joint be unrestrained.
3. At the columns along my drag strut/ expansion joint, I assume I also need to detail the roof girders to slide at the seated connection to the column? I would imagine with the dead load alone the friction would act as a restraint at the slotted seat connection, so if I want it to slide this would have to have some type of low-friction slide pad? Is this all even worth it for 3/4" expansion, or can I just take this into account and design for an additional P-delta of 3/4"?
Sorry if this got wordy, and I will post a couple of sketches if that helps. I have an excellent expansion joint article but it doesn't cover these details. Any other articles or links so I can do my own research are also welcome.
Thanks in advance.
New Building:
Wind but no seismic, in Florida
35ft tall tilt panels including parapet, roof height @ 30ft/
Steel framing interior, front side only will have offices with a second floor (steel frame and composite deck-slab) and the rest is open light industrial and warehouse.
I have selected two locations at plan geometry changes for expansion joints in the roof, and because the length of the roof requires them, dividing the roof into 3 sections. For the purposes of this discussion it can be one long rectangle with an approximate 4:1 ratio for the whole building.
1. Forgive me if this is a silly question, do I need to continue the expansion joint at the second floor also? I only have a second floor along the front side of the building that extends back about 1/4 of the building width.
My immediate response is no, the expansion joint is for the roof not the entire building. Worse case I have only 3/4" of total expansion at each joint, which includes the end and center sections.
The expansion joint(s) detail right now is along a single column line with one roof WF beam. This beam will also act as a drag strut and at one end of the building as part of a braced frame.
Both sides of the deck are mounted to two continuous plates that can slide on top of the WF with a gap in between obviously to accommodate the movement. I assume I need to let both sides of the roof float.
2. BUT- Can I rigidly connect the middle roof section along both edges and design for expansion while allowing the end sections to slide at the expansion joint? Or must both sides of an expansion joint be unrestrained.
3. At the columns along my drag strut/ expansion joint, I assume I also need to detail the roof girders to slide at the seated connection to the column? I would imagine with the dead load alone the friction would act as a restraint at the slotted seat connection, so if I want it to slide this would have to have some type of low-friction slide pad? Is this all even worth it for 3/4" expansion, or can I just take this into account and design for an additional P-delta of 3/4"?
Sorry if this got wordy, and I will post a couple of sketches if that helps. I have an excellent expansion joint article but it doesn't cover these details. Any other articles or links so I can do my own research are also welcome.
Thanks in advance.