Sep 4, 2016 #1 MFS0035 Mechanical Joined Sep 1, 2016 Messages 1 Location US Is anyone aware of fire sprinkler design criteria for rack storage of rolled carpet other than FMDS0830?
Is anyone aware of fire sprinkler design criteria for rack storage of rolled carpet other than FMDS0830?
Sep 4, 2016 #2 TravisMack Mechanical Joined Sep 15, 2003 Messages 1,775 Location US It is outside the scope of NFPA 13 criteria. The only published info I am aware of is the FM data sheets. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Upvote 0 Downvote
It is outside the scope of NFPA 13 criteria. The only published info I am aware of is the FM data sheets. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Sep 5, 2016 #3 stookeyfpe Specifier/Regulator Joined Mar 13, 2005 Messages 1,882 Location US Travis is correct. I don't have access to GE GAP and that would be the only other source other than proprietary fire test data. Upvote 0 Downvote
Travis is correct. I don't have access to GE GAP and that would be the only other source other than proprietary fire test data.
Sep 6, 2016 #4 MGXFP Mechanical Joined Jul 30, 2002 Messages 426 Location US I had a project years ago with rack storage of rolled carpet but it was stored ~5'-10' or so. I think we used 0.6/2000 with K14 storage sprinklers. Higher than that and there isn't anything I'm aware of. Upvote 0 Downvote
I had a project years ago with rack storage of rolled carpet but it was stored ~5'-10' or so. I think we used 0.6/2000 with K14 storage sprinklers. Higher than that and there isn't anything I'm aware of.