Hi everybody,
A client of mine has Robicon VFD of the Perfect Harmony Series (PWM) 3000 V, powering 800 Hp, squirel cage star connected motor.
In each phase Robicon uses a complicated combination of 5 phase-shifting transformers (delta secondary 480 V), each connected to 6 pulse rectifier, which in turn, is connected to the transistor block. Each step can generate +/- 600 V.
In order to model a sinusuidal wave form with peak of about 3000 V the steps connect in series to each other in different combination.
The problem that we are experiencing is that the filtering capacitors after the rectifier burst ( explode). We did some measurement and it seems that the whole system is floating to ground. This means that the potential on the capacitor can go up to 3000 V.
Robicon says that this is not possible, but according to the schematic they gave the client - it is exactly what would happen. The reason is that there is absolutely no grounding connection after the rectifiers. There is also no grounding of the neutral.
Is that normal? Has anybody else experienced the same problem with Robicon VFDs, and if so how was it solved.
Thanks and regards
Ted
A client of mine has Robicon VFD of the Perfect Harmony Series (PWM) 3000 V, powering 800 Hp, squirel cage star connected motor.
In each phase Robicon uses a complicated combination of 5 phase-shifting transformers (delta secondary 480 V), each connected to 6 pulse rectifier, which in turn, is connected to the transistor block. Each step can generate +/- 600 V.
In order to model a sinusuidal wave form with peak of about 3000 V the steps connect in series to each other in different combination.
The problem that we are experiencing is that the filtering capacitors after the rectifier burst ( explode). We did some measurement and it seems that the whole system is floating to ground. This means that the potential on the capacitor can go up to 3000 V.
Robicon says that this is not possible, but according to the schematic they gave the client - it is exactly what would happen. The reason is that there is absolutely no grounding connection after the rectifiers. There is also no grounding of the neutral.
Is that normal? Has anybody else experienced the same problem with Robicon VFDs, and if so how was it solved.
Thanks and regards