I guess I need to state a little more clearly why I claimed this was an LTC. A "dispatcher" to me is someone on the radio, phone, computer, or switch board; not the one wearing the gloves. If he "raises the tap" rather than ordering the operation, sounds to me like he performed it personally. LTCs are equiped with motors and controls and are easily controlled from switchboards or SCADA. Deenergized tap changers are not usually equiped with motors, but must be cranked by hand.
To those who couldn't find standards, this is from C57.12.00:
The neutral position (the position in which the LTC circuit has no effect on the output voltage) shall be designated by the
letter “N” for load tap changers. The raise range positions shall be designated by numerals in ascending order,
corresponding to increasing output voltage, followed by the suffix “R,” such as 1R, 2R, etc. The lower range positions
shall be designated by numerals in ascending order, corresponding to decreasing output voltage, followed by the suffix
“L,” such as 1L, 2L, etc. (this applies to the relationship between two windings of a transformer only, such as the H and
X windings). In the event of system requirements, such as reversal of power flow, regulation of input voltage (LTC in the
primary winding), or any unusual conditions, nameplates shall have raise-lower designations as specified by the user.
This applies to two-winding transformers only.
Me again. Clear enough until they got to the exception. How is input voltage regulated? Does an LTC located in the primary winding used to control secondary voltage qualify for the user designated exception? Kinda silly exception, since the whole standard is subject to user designation override.
Some more IEEE C57.12.10:
6.4 Position indicator
... The position indicator shall be marked in accordance with the following:
a) The normal (rated low-voltage) position shall be located on the vertical centerline of the dial,
preferably at the top of the dial, and shall be indicated by the letter “N.”
b) The raise range, when referred to the regulated (low-voltage) circuit, shall be located on the righthand
portion of the dial. A larger letter “R” (Raise), appearing only once, shall be located in the
right-hand half with an arrow indicating the direction of raise. The sixteen tap positions in the raise
range shall be marked, and a number shall appear opposite at least every fourth position. Number
16 shall be the highest voltage position (see Figure 5).
c) The lower range, when referred to the regulated (low-voltage) circuit, shall be located on the lefthand
portion of the dial. A large letter “L” (Lower), appearing only once, shall be located in the lefthand
half with an arrow indicating the direction of lower. The sixteen tap positions in the lower
range shall be marked, and a number shall appear opposite at least every fourth position. Number
16 shall be the lowest voltage position (see Figure 5).
Later,