Fraser21
Electrical
- May 18, 2010
- 8
Looking for some insight on a problem I’m running into. Doing some troubleshooting at a satellite dish site, Main breaker has a reverse power, and a directional relay along with an over current relay. The board has a sole purpose of feeding de-ice heaters to melt ice off of the big dishes during the winter. We have isolated all ties to the board and are just running off of the utility main and de-ice feeder breakers. None of which have ground fault. When the resistive load from the heaters comes on, and sometimes when the load comes off the board the directional and reverse power relay both pickup and sometimes trip the 86 and take out the main...any idea what would cause this?