We are retrofitting an old AEG turbine/generator with new protection and the old circuits show that the reverse power relay has a hardwired pressure interlock in the short time reverse power trip, the long time trip in unaffected. Can anyone shed light on what this is for?
 
Replies continue below

Recommended for you

I would assUme the pressure is a stage pressure, thus representive of turbine mechanical power.

I'm not familar with AEG control phylosipy so I don't know there reasoning.

Could it be there incase some type of generator fault caused a monetary reverse power, with the turbine at power, it would NOT open the breaker.

I Know one company's scheme was to use a combination of valve closed limit switches which indicated steam flow was blocked before arming reverse power breaker trip. I could see a stage pressure being the same.
 
Hi.
"I Know one company's scheme was to use a combination of valve closed limit switches which indicated steam flow was blocked before arming reverse power breaker trip. I could see a stage pressure being the same."
I know one company that used only steam flow/pressure as indication of main valve closed position ( via PLC) w/o limit switch.
For my pinion, in new numerical relay you can use this signal for the reverse power short time block.
Regards.
Slava

 