Retaining wall repair rec
MAEngr
10
I am evaluating an exterior retaining wall that a contractor built to prescriptive codes. They came back after inspection and added two feet of additional retaining height which means insufficient rebar in the wall and inadequate footing sizes. The wall is starting to bow in the middle. The owner would like to not demo and rebuild the wall. My thoughts on repair would be to add a haunched wall butted against the existing wall with dowels and to add additional concrete/rebar to the footing. Is this the approach you all recommend? They would also be open to a buttress wall in the middle on the exposed side since that side is downhill and not visible. I don’t like this option as much.
We've used EPS foam blocks to deal with this in the past. Always worked out great - used about 3 ft. of soil/gravel on top with a thick membrane on top of the blocks. EPS will melt if exposed to petroleum substances.
One other thought I had was to excavate 9 feet of soil behind the wall and replace with geofoam to help greatly reduce the stress on the wall. While the soil is excavated I would also have the contractor epoxy any cracking on the heel side of the wall. This seems like a viable solution to me that doesn’t involve tearing down the wall. Thoughts?
If you can excavate behind the wall, the geofoam option can probably be made to work, but you consider reinforcing the soil mass - creating a mechanically stabilized earth (MSE) wall behind the block wall, also. We typically have the internal design done by the geogrid supplier, so we only deal with the external stability design.