Resonable to ask?
cdafd
Specifier/Regulator
So 20 plus year old sprinkled building.
Originally a food store, but has been vacant over 10 years.
A mercantile store wants to come in and occupy a portion of the building.
Plans submitted showing 120 sq ft spacing on sprinklers.
1. No hazard specified.
2. No hydraulic calculations submitted.
SO, I am thinking minimum specify the hazard.
So, should the ahj ask for Calculations on top of that??????
That's a broad canvas. Is it high piled combustible storage? Is it high piled combustible storage with hazmat? Is it Sketcher's shoe store with back-to-back shelving units of cartoned, unexpanded Group A plastics? 20+ years old doesn't tell me everything either. Is it a pipe schedule system? Are the sprinklers > = 50 years of age?
If you're unsure seek a Technical Report and Opinion per the IFC or NFPA 1.
Should be hydraulically calculated when installed.
Not high piled
Thank Dolar store
Sprinklers less than 50 years old.
I would think they need to show maintenance per NFPA 25 on anything that is being kept. Also, I would think they need to do a flow test and calcs. The building was vacant 10 years. Has the water supply changed? What condition is that piping?
I would want an Owner Certificate as shown in NFPA 13. I would want hazards noted on the plan. Basically just have them follow the chapter on working drawings.
Travis Mack, SET, CWBSP, RME-G, CFPS
MFP Design, LLC