Many manufacturers have specifications for contact resistance in their acceptance/maintenance testing information.
In the absence of this data, you can derive some useful information from checking like equipment, i.e., you have three contactors, two of which have contact resistance in the 60-70 microohm range and one with readings in the 2-300 range. You'd be wise to suspect a problem with that errant unit assuming it is indeed the same rating for current and voltage. The same goes for each of the contacts in the contactor. If one diverges from the other by more than 50%, then it is suspect.
Lastly, on legacy (read 'so old nobody's seen a manual in decades') equipment, look at the I^2*R loss across the contactor. I always operated on the supposition that if an air-breaker contactor had more than 25 watts loss at rated current, there was going to be an issue due to the equipment's ability to deal with heat in the contact assembly.
Some air-break contactors have a bad characteristic of contacts 'glazing' over with an oxidized layer that renders high readings at the low voltages that test equipment uses. Proper cleaning will often correct this problem.
old field guy