Lburg -
You have probably been given a very simple project that is very easy to over-engineer. Your geo-tech gave you a soil strength level that will work for any standard foundation design, although the soil may be shown to be substantially better.
Take a look at the IRC 2006 - Chapter 4 - Foundations.
If the home you are designing for is a typical structure there is really no need for detailed calculations to comply with the codes and requirements. It has been done many times before you. If you choose to do so, you can do a detailed analysis, go partially mad trying to make assumptions, run up the cost and be unduely criticized. Take a good hard look at the section of the code and try to understand it, keeping in mind you have to think in 3 dimensions with continuity and not just a narrow 2 dimension snapshot.
You will find some things that are approved, legal, logical, proven and scarry!!
1. Minimum footing footing width for a basement on a one story brick veneered wood frame home or a concrete block home with 1500 psf soil is 12"!! Not really surprising since 40 years ago (and today) wood basement panels were permitted without concrete footings by using 8" of compacted gravel.
2. The minimum compressive concrete strength is 2500 psi, despite most contractors minimums of 3000 or 43500 psi.
3. Thanks to a knee-jerk reaction (possibly erroneous) from the requirements for weaker, sectional discontinuous panel wall systems, the 2006 IRC has adopted the anchor bolt spacing between 8" and 12" as opposed to the previous requiremnts of 6' and 2' from the end of a sill. Some jurisdiction have over-ruled this point and have reverted to the traditional spacing for continuous walls (masonry and poured concrete).
4. When referring to Table R404.1.1(1), for PLAIN (unreinforced) masonry walls, the thickness should be 8", 10" or 12" depending on the wall height and the height of retained backfill. For REINFORCED 8" masonry walls the reinforcement will be #5 or #6 @ 48" o.c. For 12" REINFORCED walls, the reinforce would be #4 or #5 @ 72" o.c.
5. There are also tables for reinforced concrete walls, and ICF walls.
To put things in perspective, read the code carefully and try to understand the rationale. I am sure you can increase the code minimums to something realistic and comparible to standard construction that has been proven.
In addition to the above mentioned code, you can make your own detailed design and campare to what has be proven to be acceptable. You will find the results and differences very revealing when you step back and look at the big picture.
You will have to determine if the home fits into the applicable requirements of the code. The true features of a successful basement/foundation design is the correct provisions and specifications for subsurface drainage, backfill and surface water control.
If have spent about 40 years trying to calculate why a masonry basement works so well and still am challenged. To me, it is much more difficult to get precise on a small basement than it is to design a 20 story loadbearing masonry structure.
Dick