- Aug 9, 2012
- 1
I have several fans that are operating about 17% too fast. The applicator is Air Turnover Units which are too large for the load and also too noisy (exceeding the specified dB) . The contractor who installed them will resheave for free, but he has suggested we run these on VFD' - which will coast $100,000 (less incentive from Duke Power so my final cost will be $53,000).
He says the VFD's will save enough energy to pay for themselves in a year - which I am sure is true (but I need $53,000). If we sheave, the noise problem goes away (there is no concern for the load) - but will I save that much power?
I ask because the applicable affinity law is apparently based on "speed". The flow is reduced by fan rpm and the power to turn that fan is reduced by old-Power x (new speed/old speed)3 ... but resheave does not impacting the speed of the MOTOR.
Make sense?
I'm unclear how to estimate the savings. The contractor (a reputable design-engineer-build company) is dragging his foot coming back with the answer to cost saving based on resheave.
Thanks
He says the VFD's will save enough energy to pay for themselves in a year - which I am sure is true (but I need $53,000). If we sheave, the noise problem goes away (there is no concern for the load) - but will I save that much power?
I ask because the applicable affinity law is apparently based on "speed". The flow is reduced by fan rpm and the power to turn that fan is reduced by old-Power x (new speed/old speed)3 ... but resheave does not impacting the speed of the MOTOR.
Make sense?
I'm unclear how to estimate the savings. The contractor (a reputable design-engineer-build company) is dragging his foot coming back with the answer to cost saving based on resheave.
Thanks