I am trying to get my basement finished, and I want to remove 2 brick columns (6'-8" o.c.) which are supporting a full size (not dimensional lumber) 4" x 12" wood beam. There are other masonry columns which support this wood beam also spaced 6'-8" o.c. but I am not touching them. I want to remove 2 columns which will give me a ~ 20' span in the basement from the 3rd column to the outside foundation wall.
The wood beam is supporting full dimension 2" x 12" floor joists (for the first floor). The full length of the 2"x12" joists is 27' and the house spans ~ 30' in the other dimension (that is the length of the 4" x 12" girder in the basement). It is an old big house, 2 floors and a walk up attic.
Now, I did the calculations on the loads for the replacement beam, and I got ~ 2,360 lbs / lf based on the building code in N.Y.C. where:
live loads are 40 psf / 20 psf dead load living areas, (plus 8 psf for partition walls)
30 psf LL / 20 psf DL for sleeping areas, (plus 8 psf for partition walls)
20 psf LL / 20 psf DL for attics , (plus 8 psf for partition walls) and no roof since load travels down to outside bearing walls.
Tributary width of 14.6667'.
I looked up tables for Parallam and I can get a 7" x 16" that will cover the 20' span I am looking to open in the basement. My wife threw in the monkey wrench when she said that she is not looking to give up 4" of head room (since the existing wood beam is 12" deep, and the new Parallam would be 16").
So normally, I looked up tables for steel beams, and that's when I ran into problems, the steel beam tables were telling me to use W14x26 for a tributary width of 16' (inclusive of my 14.667') with a maximum span of 13'7, when I need 20 ft. This is for Fy = 36ksi.
Are there stronger beams I can use Fy=50 ksi, or can I use let's say W10x22 which max span is 11.7 ft and double it up side by side?
Thanks,
Thanks,