- May 17, 2001
- 2,374
The general contractor to a 7-level concrete building consisting of 4 levels of residential and 3 levels of parking (all above ground) constructed the perimeter rectangular columns to the parking level using steel formwork, then after stripping the forms, constructed the concrete structural walls that are orthogonal to the long-axis of the column. 36"x12" columns with 8" walls that infill between the columns that are on 25' centers.
The contractor did not provide any horizontal reinforcement between the wall/column interface, nor was there any effort to roughen the off-form finish to the columns prior to constructing the walls.
The walls are part of the main lateral force-resisting system.
I have looked at more 'conventional' repair techniques like 1) drilling and dowelling in rebar and CIP concrete, and 2) horizontal steel through-bolts that pass though the columns 12" width and anchor to adjacent walls, with required fire protection.
I also looked at carbon FRP options to horizontally tie the adjacent walls through the columns, but without any mild steel rebar I am hesitant to rely upon a brittle materials like FRP, even if I downgrade the stress/strain levels.
Has anyone undertaken successful reinstatement of such a situation, and care to share their method/s?
Thank you.
The contractor did not provide any horizontal reinforcement between the wall/column interface, nor was there any effort to roughen the off-form finish to the columns prior to constructing the walls.
The walls are part of the main lateral force-resisting system.
I have looked at more 'conventional' repair techniques like 1) drilling and dowelling in rebar and CIP concrete, and 2) horizontal steel through-bolts that pass though the columns 12" width and anchor to adjacent walls, with required fire protection.
I also looked at carbon FRP options to horizontally tie the adjacent walls through the columns, but without any mild steel rebar I am hesitant to rely upon a brittle materials like FRP, even if I downgrade the stress/strain levels.
Has anyone undertaken successful reinstatement of such a situation, and care to share their method/s?
Thank you.