To all,
My question deals with sizing of a relief valve for a 19% Aqua ammonia (also called ammonium hydroxide) tank.
The tank is ~55,000 gallons, 14 ft diameter and was purchased as an ASME Section VIII pressure vessel. MAWP is 30 psig. The tank is located in an area remote from any other plant components.
As I see it, the pressure relief valve for this storage device should be sized for 1) possible fire case - (API-520 methodology) or 2) maximum fill rate case -100 gpm.
My question is this:
If I size the PRV for the fire case, I would get a 6" x 8" valve with a large orifice ( this is due to the large tank area) or if I size the valve for the "fill rate" case, I get a 1"x 2" valve due to the low fill-up rate.....
Does this all sound reasonable ?
Am I missing any design considerations here ?
( see for a typical tank layout)
Help from anyone with experience is appreciated !!!
MJC
My question deals with sizing of a relief valve for a 19% Aqua ammonia (also called ammonium hydroxide) tank.
The tank is ~55,000 gallons, 14 ft diameter and was purchased as an ASME Section VIII pressure vessel. MAWP is 30 psig. The tank is located in an area remote from any other plant components.
As I see it, the pressure relief valve for this storage device should be sized for 1) possible fire case - (API-520 methodology) or 2) maximum fill rate case -100 gpm.
My question is this:
If I size the PRV for the fire case, I would get a 6" x 8" valve with a large orifice ( this is due to the large tank area) or if I size the valve for the "fill rate" case, I get a 1"x 2" valve due to the low fill-up rate.....
Does this all sound reasonable ?
Am I missing any design considerations here ?
( see for a typical tank layout)
Help from anyone with experience is appreciated !!!
MJC