The image below is taken from the FIB document on precast connections and illustrates some of my concerns. Tell me those sketched failure modes don't get your pulse racing a bit?
I'm fairly confident that most well detailed systems could undergo the redistribution required to survive
flexurally without the top steel. However, when we make our redistribution argument as engineers, we rarely seem to consider the shear condition other than at the "field of dreams" end state. The truth of the matter is that shear needs to work at that end state and all intermediate points in time along the load history from zero to that end state. Including reversals if required.
As an interesting aside, most codes limit the amount of moment redistribution that designers can employ to reduce elastic moments. In Canada, it's around 15%. In many other code, the allowance is much more liberal and often based explicitly on strain and reinforcing ratio. So, if one assumes a pin (zero moment), and the elastic moment was anything other than zero, then technically your %redistribution was 100%. Not sure how we feel about that at faux pins.
chekre said:
Do u think your above statement is applicable also for end pinned beams having some minimal top bars - less than the 1/3 that u have proposed or it is just for beams having none at all of top bars ?
Honestly, I don't know the answer. I'll share some thoughts instead.
1) I consider
no top steel to be a definite show stopper per our previous discussion and the clip below.
2) If you show me a gigantic, continuous transfer beam with 4-15M as the nominal top steel, I'll veto that (this has happened to me on multiple occasions).
3) In practice, if I've got 1/3 top steel and and it extends at least 0.25 x clear span, I'll sleep pretty easy. This is what I generally do at faux pins.
4) In my heart of hearts, I question the validity of any shear design at a location not designed for the expected moment at that location limited to a fairly modest amount of redistribution. While we, as designers, often treat shear and moment capacity as independent, they usually are coupled phenomena. Remember all the dust up a while back when that university of Michigan study indicated that stud rail punching shear provisions were non-conservative? Turned out they were non-conservative when insufficient flexural reinforcing was provided.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.