Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Regulation of the mains voltage down in 3 phase system

Status
Not open for further replies.

homoly

Electrical
Jun 11, 2007
100
Hello,

I am solving now a problem how to regulate down mains phase voltage in 3 phase system from 230VAC to 170 VAC. My first idea was to use transformer with one part with fixed ratio + in secondary connection of various secondaries in series. The problem is the huge variation of currents in secondary ( 170 VAC may be requiered at few tens of Amp and also few hundreds of Amp as well at the secondary ).

For this reason I have found some alternatives:

1.) Synchronous generator
2.) Induction regulator

Are some other alternatives to solve this issue except 2 mentioned above ?

Any advice will be appreciated.

Gabriel.
 
Replies continue below

Recommended for you

Why??
If you tell us the application we can help with the solution. What is your load?
What are your regulation limits?


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
The input should be 3x400VAC 50 Hz delta output variable from 3x 170*sqrt(3) up to 3x 230VAC + Neutral.

This output voltage range should be avaiable for currents from 60A to 600 A / phase, now the particullary important area for me is 170V-180V area.

The aim of this system/device would be test system performances at the worst case low mains for various machines.
 
Bill,

Thank you. I will check the links.
 
Status