13.2.3.6 Redundancy factor. Some nonbuilding structures are designed with parameters from Standard Table 12.2-1 or 15.4-1 if they are termed “nonbuilding structures similar to buildings”. For such structures (assigned to Seismic Design Category D, E, or F) the redundancy factor applies. Pipe racks, being fairly simple moment frames or braced frames, are in the category similar to buildings. Because this structure is assigned to Seismic Design Category D, Standard Section 12.3.4.2 applies.
Considering the transverse direction, the seismic force-resisting system is an ordinary moment resisting frame with only two columns in a single frame. The frames repeat in an identical pattern. Loss of moment resistance at the beam-to-column connections at both ends results in a loss of more than 33 percent in story strength. Therefore, Standard Section 12.3.4.2, Condition (a) is not met. The moment frame as described above consists only of a single bay. Therefore, Standard Section 12.3.4.2, Condition b is not met. The value of ρ in the transverse direction is therefore 1.3.