Three phase fault close to generator causes sudden load throw-off on the machine (phase fault is mostly inductive). This could cause machine speed to go up. The impact is great, especially when the generator is not part of any large grid.
Faults are inevitable but reclose is a choice we make.
Reclose on ground faults shouldn't pose a problem.
Moreover, majority of faults in overhead lines are supposed to be ground faults anyway!