samy81, regards treading on your thread.
tem1234, i am not sure for the derating question in my experience that comes from oil breakers, but has no effect in the gas cb. a gas cb is designed to withstand the rated interruption. most cb's either have logic built in (most commonly an Agastat time delay) in the closing circuit, or have a delay in the relaying - this is not required for the first operation.
the timing that i am aware of for a spring mech cb as a recloser can have an immediate O-C, and O- then a short time delay - required to charge after opening again ~13seconds, and then the final time will stay open to be reset manually.
if there is a hydraulic mech it can go for 6, sometimes 7, operations before being recharged.
this is a scheme that i am familiar with. would like to hear of others.