picsta:
I'm not sure your mean "evaporative" losses; but I'll have to take you at your word.
A water cooling tower does its cooling by evaporating a % of the feed water to the atmosphere. This is the key to the whole operation of "cooling". No evaporation - no cooling (& no foolin'). A cooling tower works on the principles of simultaneous heat and mass transfer. The mass transfered is the evaporated water. This evaporated water is not a "loss". Rather, it's the price you pay for the ride.
Now entrainment and "mist" losses, that's another story. These should not occur in a well designed tower. But if you're short of water in your shopping centers, then the cooling could have been designed to employ air-fin cooled condensers for your A/C system (I assume that's the load being imposed by the shopping center).
Recapturing the water evaporated is going to take energy and investment. And, as they say in my wife's native Peru, "the price of the price of the laundry bill is going to exceed the price of a new shirt". Once the water is diffused into the atmosphere, it's next to hell to try to get it back. It's like trying to seed a rain cloud, hoping it'll rain - and with little or no chance that it will. I frankly have never heard of anyone even debating any attempt to recover evaporation losses.
Sorry.