This week we had an interesting situation here that still has some of us scratching our head. We have an industrial customer that is supplied by two parallelled pad mounted transformers. The primary voltage is 12,470/7200 GND-Y. the secondary is 480/277 GND-Y. Both transformers were installed four years ago as brand new 1500 kVA units, with identical impedances of 5.14. The secondaries were connected to a common bus by five, 500 MCM copper conductors per phase. The primary was fed thru transformer one to transformer two.
The secondary of transformer two reached a temperature great enough to ignite the oil that had leaked into the secondary compartment. we do not know if the temperature caused the oil leak, or if the lower level of oil caused the extreme temperature. The transformer has been sent for testing and evaluation.
The only difference between the two setups that we can find is the length of the secondary conductors. The conductors of transformer two are about 2' shorter than the conductors of transformer one. The total length of the transformer two secondaries is about 15'.
Can this be the cause of the temperature increase in transformer two?
We have had to install an emergency replacement transformer with an impedance of 5.77. Amp readings on the secondaries of both transformers differ by about 2%. Full load measured on either secondary max out at 1450 amps, so neither transformer is overloaded. The customer only operates one shift each day.
Any ideas? Are we just waiting for the replacement to fail?
Happiness is a way of travel, not a destination.
The secondary of transformer two reached a temperature great enough to ignite the oil that had leaked into the secondary compartment. we do not know if the temperature caused the oil leak, or if the lower level of oil caused the extreme temperature. The transformer has been sent for testing and evaluation.
The only difference between the two setups that we can find is the length of the secondary conductors. The conductors of transformer two are about 2' shorter than the conductors of transformer one. The total length of the transformer two secondaries is about 15'.
Can this be the cause of the temperature increase in transformer two?
We have had to install an emergency replacement transformer with an impedance of 5.77. Amp readings on the secondaries of both transformers differ by about 2%. Full load measured on either secondary max out at 1450 amps, so neither transformer is overloaded. The customer only operates one shift each day.
Any ideas? Are we just waiting for the replacement to fail?
Happiness is a way of travel, not a destination.