Structural
Aug 20, 2015
27
Hi, I need expert opinion on possible reasons for cracks shown in attached pictures.

Element - basement ground slab
Thickness - 450mm
RF details - T1, T2, B1, B2-T16@200 (QT bars)
Clear cover - 50mm
Ambient temperature during casting - 27-30 Celsius. (Sri Lanka 6pm to 6am)
Mix design (kg/m³):
Cement - 391
Fly ash - 106
Coarse aggregate - 1003
Manufactured sand - 726
Water - 174
 

Attachments

  • 1741445394106.jpg
    1741445394106.jpg
    534.4 KB · Views: 52
  • 1741445393974.jpg
    1741445393974.jpg
    438.4 KB · Views: 46
  • 1741445394062.jpg
    1741445394062.jpg
    398 KB · Views: 42
  • 1741445394019.jpg
    1741445394019.jpg
    355.1 KB · Views: 40
  • 1741445394150.jpg
    1741445394150.jpg
    374.1 KB · Views: 37
  • 1741445394234.jpg
    1741445394234.jpg
    404.1 KB · Views: 36
  • 1741445393932.jpg
    1741445393932.jpg
    556.2 KB · Views: 36
  • 1741445394194.jpg
    1741445394194.jpg
    519.4 KB · Views: 52
Replies continue below

Recommended for you

I guess early age cracking . The reason should be early-age volume change due to thermal deformation , cement hydration and shrinkage .
Can you check the range of crack depths and measure the widths?
 
That’s not how expert opinions work. You’re soliciting guesses. Crack causation determinations are extremely involved; there are literally dozens of reasons (often interrelated) why concrete might crack. It could be as simple as mapping/measuring cracks, or it could require petrography, identification of points of restraint as well as reactive aggregates or sources of sulfates/chlorides, consideration of temperature exposures and load cycles, an analysis of the mix and placement, etc.

Here’s my guess: it’s concrete, therefore it cracked. That’s the reason.

You might as well feed this to an AI until you get a preferable answer.
 
I guess early age cracking . The reason should be early-age volume change due to thermal deformation , cement hydration and shrinkage .
Can you check the range of crack depths and measure the widths?
I will visit the site tomorrow and update. BTW, what are the simple methods of checking crack depth. I have a tool for measuring crack width.
 
First might be plastic shrinkage in small area. Last is crazing. Others look restrained shrinkage.
 