jmmr
Electrical
- Jul 10, 2008
- 2
I am trying to read a parameter from a Kollmorgen S300 servo drive over Profibus using an S7-300 controller and Step 7 program. I have setup the program per the Kollmorgen manual ( task ID = 1, Parameter Number = 1724, Parameter Index = 1. I send out the command to the drive but the response back does not change from a previous write to the drive. Can anyone offer some tips to what I may be missing?