Help Request
Hello Guys
i have a Sinamics G120C PN error, when trying to execute the Start Command through the Starter software it gives the following error Message: "the switch-on disable of the drive is active " in addition to this, the diagnostic buffer shows that there is a missing enables.
IMG20220801102449_gzcppy.jpg

how can i eliminate this error inorder to have manual test of the drive through the Starter software.
Thanks in advance
 
It might be because you are in commissioning mode.

This is from Siemens support and may not apply to your drive.

you drive is in commissioning mode so you can't switch on the drive!
Set p9 of the driv to 0 to leave this mode.


“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
 