I had only a few minutes to look at your model at lunchtime today and won't have any more time until next week. Unfortunetely, I'm also a bit rusty with EPANET, since I haven't used it in about two years.
Even so, I was able to find and fix one of the errors. The Status Report says that Dv4 is disconnected. Actually it's DV4 and its neighbors that are disconnected from the rest of the network. EPANET can handle isolated regions, but they must have a source, which this region does not. I added a pipe between nodes Dum6 and Dum126 and that took care of this problem.
The Status Report also says that your reservoir is closed, which would mean the model doesn't see an active source. I exported the network file (File|Export|Network) and saw that all of the pipes are open, so I can't figure out why the reservoir would be closed. I added a second reservoir with a higher head (1000 m) and connected it directly the system somewhere, that didn't work. The Status Report said my reservoir was closed also, even though I set its status to open.
I then tried closing all three pumps and bypassing the pumping station with a new pipe between the reservoir and node D8, increasing the head on your reservoir, connecting "disconnected" nodes with more pipes, giving all demand patterns a non-zero value at all time steps (I changed your zeros to 0.1), etc.. None of this worked for me.
This is going to take a bit more digging. One thing you might want to do, since you know this model much better than I do, is export the network file and see if you can spot something in your inputs that might be causing this problem.
Fred
--Winston S. Churchill