Hello Gents
We have just replaced a 120kVA UPS on an oil & gas platform with a newer identical UPS. The original had 34 critical supplies fed from a distribution which all had 300mA RCD's on them.
The new system had the same 34 MCB's but a were supplied with 30mA RCD's by mistake!! this was not picked up at FAT so we have what we have at the moment!
Anyway, the way I see it is that critical UPS supplies are not normally fed from an RCD circuit whether it is 30mA (personal protection) or 300mA (fire/ equipment protection).
We are trying to justify the removal of all of the RCD's and just leave the correctly rated MCB's. Do you guys have any comments on why this would not be advisable?
Thanks as always for your input.