RCD protection

Status
Not open for further replies.

richerdick32

Electrical
Joined
Feb 22, 2014
Messages
16
Location
GB
Am I correct in thinking that if a rcd feeds a transformer, then anything connected to the secondary of the transformer will not be protected by the rcd and another rcd is required to provide protection
 
Yes.
But only if it is an autotransformer (no isolation between primary and secondary).

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
sorry just to be clear an rcd on the primary of an auto transformer would provide protection to secondary circuits as they are electrically connected
An rcd on the primary of a normal transformer ie two electrically isolated coils would not provide protection to the circuits on the secondary
is that correct
 
Yes, that is exactly what I said.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
I'm confused.
Did you mean to say "Unless" rather than "But only if" ??
On the other hand I'm still on my first cup of coffee this morning.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
You are right to be confused, Bill.

Of course it should be "unless". I think that richerdick got it. And that was NOT exactly what I said.


Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 