pristava
Industrial
- Jan 8, 2004
- 53
Industrial Power System provides five transformers 13.8 / 0.6 kVolts - 2000kVA - 3pcs, 225kVA - 1pce, 150kVA - 1pce,
(a) 2000 kVA transformer has 1926 Amps on secondary side, but 3000 A bus is connected there with 3000 A main breaker.
(b) also, 150 kVA transformer has 144 Amps on secondary side, but 200 A bus is connected there with 200 A main breaker.
I discussed with Senior Electrical Engineer about that - especially about a situation that 2000 kVA transformer gets a load 3000 A on secondary side ( or 150 KVA transformer load 200 A). In both cases transformers are overloaded almost 50 %.
He said that there is NO problem because that situation will be solved by Protective Relaying.
My question - Can that One Pole Diagram be accepted by our Professional Engineer, and stamped by him after that ?
Note : Network is radial.
(a) 2000 kVA transformer has 1926 Amps on secondary side, but 3000 A bus is connected there with 3000 A main breaker.
(b) also, 150 kVA transformer has 144 Amps on secondary side, but 200 A bus is connected there with 200 A main breaker.
I discussed with Senior Electrical Engineer about that - especially about a situation that 2000 kVA transformer gets a load 3000 A on secondary side ( or 150 KVA transformer load 200 A). In both cases transformers are overloaded almost 50 %.
He said that there is NO problem because that situation will be solved by Protective Relaying.
My question - Can that One Pole Diagram be accepted by our Professional Engineer, and stamped by him after that ?
Note : Network is radial.