They are apparently trying to teach on a subject which is a fairly common problem/error for young engineers, drafters/designers and builders. And, that is, that LL’s are expressed as loads in lbs./sq.ft. (whatever units) projected on a horiz. plane. However, we typically calc. (sum up) DL’s w.r.t. their own primary plane, such as the fl. sheathing for a fl.system, or that roof system w.r.t. its sheathing plane. Then, the DL must be converted into a slightly greater load (13/12) in lbs./sq.ft. projected on the horiz. plane, so the LL and DL can be combined. It is fairly common practice then, to use the horiz. length as the beam length to do normal beam calcs., with due consideration for the potential of horiz. thrust or axial loads on the members and supports. This is basically what BA and SRE and some others have done, without the above discussion.