Berniedog
Structural
- Dec 19, 2005
- 200
On a project with footings with piers for High School Bleachers, the 7 day concrete breaks came in at 1420 psi amd 1320 psi. THE specified concrete was 3000 psi. Assuming the 7 day strength is 75% of what will be the final strenght, this concrete will be under 1900 psi. The minimum code (2006 IBC) specified concrete strength is 2500 psi.
I cannot find any literature that states what the consequesnces are for 1900 psi concrete. I checked the development length of the rebar and it is OK since I over designed the reinforcing steel some. I believe the concrete will not hold up to the freeze and thaw.
Any ideas?
I cannot find any literature that states what the consequesnces are for 1900 psi concrete. I checked the development length of the rebar and it is OK since I over designed the reinforcing steel some. I believe the concrete will not hold up to the freeze and thaw.
Any ideas?