Hydrocad is based on the SCS drainage methods. Many of the SCS items (such as Curve Numbers) have remain unchanged since their original inception, back in the 50's.
The SCS was charged with devising a method to estimate runoff, to prevent massive erosion like that which occured 20 years prior (the 1930's dustbowl.)
The numerical methods scientists and engineers had at their disposal were limited to tabular information, slide rule computations, and other "analog" items. (Of course, a skilled operator could perform long divsion carried out to the fourth decimal on a slide rule, but that had to be laborious.)
These SCS methods, the rational method, and then the modified rational method were originally designed in terms of square miles.
not hundreds of square feet!
It is my opinion that municipalities and other regulatory agencies that require designers to model subcatchments down to the nearest 100 square feet are abusing the software.
Can you trust an emperically derived curve number, one that was tested on ground cover in test plots of square miles, and linearly scale that down to the contributing area of a sinle catch basin?
Just because a PC can divide a number by 43,560 does not mean the answer is correct.
I suggest you keep your subcatchments as big as possible, because the runoff CNs are not appropriate for tiny subcatchments.
Other mis-use of the software:
I have recently had a reviewer ask me to determine the potentional pressure head of a 6" perforated underdrain that was designed to be draining a rock filled trench, because if the drain were to operate under a pressure head, the capacity of the underdrain would be limited, and then the rock filled trench would drain slower than the model indicates.
It would drain slower than the model indicates because HydroCAD can not handle a pipe flowing full, and is limited to open channel flow in pipes.
The manual is direct and upfront about this limitation, and suggests users apply the dynamic storage indication routing method, to include the tailwater effects on pipe systems when trying to model catch basins.
So now the model needs to model the tiny subcathments that contribute to individual catchbasins, the culverts connecting them with a tailwater analysis, and also a pond with insignificant storage at the daylights of underdrains.
How's that for keep the model simple?
___
Craig T. Bailey, PE