Can anyone help - I am upgrading a building supply to 1000KVA at 400V and installing new switchgear and a standby generator. The client has a spare generator rated at 1250KVA. The electrical contractor says the size of the main switchgear should be based on the rating of the generator not the incoming power supply which means we need 2000A rated incoming MCCB's (generator amps = 1800A max).
I don't agree with this as I think the generator can't supply more than the actual building load - which means I can use MCCB's rated at 1600A. Is this ok?