Query on Flexural Shear Cracking of Postentioned Prestressed Beams
kww2008
AU
My query relates to the determination of V_0 = M_0 /(M*/V*) for continuous indeterminate post-tensioned prestressed beams in AS5100.5 Clause 8.2.7.2. My understanding of the steps is:
The precompression moment, M_0, is determined using the total unfactored prestressed moment, i.e. primary prestressed moment plus secondary prestressed moment.
M* and V* determined from ULS applied moment and shear, excluding the effect of secondary prestressed effects.
Calculate V_uc using using 8.2.7.2(1) for flexure shear cracking capacity and 8.2.7.3(4) for web shear cracking capacity, and the lower of these two capacities is to be greater than V* (V* here includes the effect of secondary prestressing effect).
Are the above steps correct/appropriate ?
Correction and modification to my earlier posting:
I can think of two approach to calculate phi*Vuc for an indeterminate beam. Which of the two is more appropriate, or is there a different way of doing this ?
Approach 1
Calculate phi*V_uc using using 8.2.7.2(1) for flexure shear cracking capacity and 8.2.7.3(4) for web shear cracking capacity, and the lower of these two capacities is to be greater than V* (V* here includes the secondary prestressing effects).
Approach 2
Consider the secondary prestressed effects as effects from a load, and use the steps below:
The precompression moment, M_0, is determined using the unfactored prestressed moment, (P/A +- Pey/I)
M* and V* determined from ULS applied moment and shear, including the effect of secondary prestressed effects.
The prestressing secondary effects are considered to be an external loading in AS3600 as they are in most codes, so Approach 2 above!