Hello,

There is a process plant with some pumps pumping fluid out of the plant
I use 2545*P*((1-eff)/eff).FUM.FLM classic pump motor heat dissipation formula from ASHRAE fundamentals handbook for these.

Now there are a lot of other pumps in this plant which only carry fluid between H/Xs, evaporators, indoor tanks etc. and fluid they pump is just transferred to the next process within the plant. Both pump and motor is indoors.
Do I use 2545*(P/eff)*FUM*FLM formula in this case?

This equation is giving me HUGE load, but hey- if it is the correct equation so be it.

Thanks!

eff=pump motor's efficiency
FUM=motor use factor
FLM=motor load factor
 
heat dissipation from a motor doesn't care about where the pipes go. so the equation should be used.
I'm more concerned on how you get the efficiency since that depends on operation.
 
Herr, thank you for reply but I do not agree with you. Motor efficiencies are estimated from ASHRAE tables..

It seems like this question has been answered before:

The correct equation to use in my case is

2545*(P/eff)*FUM*FLM

P=rated horsepower of pump's motor
eff=pump motor's efficiency
FUM=motor use factor
FLM=motor load factor
 