I am performing a field test of the pumps at our water treatment facility. While I know it is necessary for the pressure guage to be located between the throttling valve and the pump, is it necessary for the meter to be in the same area as the pressure gauge? The flow does not empty to atmosphere. It is under a constant head of the clarifier.
I ask this because when plant personnel performed a test years ago, they throttled the valve in the intake building where they read the pressure on the guage to get the head before the throttling valve but took the discharge rate by an existing magmeter in our pipe gallery at a point 1000 feet from the intake building (throttling valve point) at a difference of 25' in height. I think their results were skewed but I'm not sure.
I ask this because when plant personnel performed a test years ago, they throttled the valve in the intake building where they read the pressure on the guage to get the head before the throttling valve but took the discharge rate by an existing magmeter in our pipe gallery at a point 1000 feet from the intake building (throttling valve point) at a difference of 25' in height. I think their results were skewed but I'm not sure.