hippo11

Structural
Joined
Mar 21, 2003
Messages
161
Location
US
What kind of limitations, or what parts of the ACI code, dictate what kinds of horizontal curves and turns you can make with a continuous PT strand in plan?

Too sharp a turn would probably cause a huge horizontal PT force, but I can't find anything on this...

Thanks!
 
I have an old PCI Post-Tensioning Manual, First Edition, 1972, that states:

Vertical deviations of tendons - 1/8" to 1/4".

Horizontal plane deviations which may be necessary to avoid opneings, ducts, chases, etc. should be have a radius of curvature of not less than 21 ft.

There is most likely a more current edition to this. Also, you might try the PCI website for more info:

 