rashy70

Electrical
Feb 19, 2009
7
I have to connect outdoor type 600VA, 33kV/220v PT thru protective fuses at the primary to 33 kV (line to line) . The supplier has provided 24kV, Siba make outdoor type , e=442mm ,Ia= 40kA fuses, is it Suitable ?. Please guide me.
 
Replies continue below

Recommended for you

If the 33kV system is effectively grounded and the PTs are all connected line-ground on the 33kV side then the 24kV fuses should be sufficient.
 
PT is connected between Line to Line of 33 kV System.
 
Then you must have 33kV fuses. But line-ground is a far better connection.
 