Struggle66,
Part of the problem when we design concrete members is that we design reinforcement for flexure and then check shear separately, but they are not separate, shear adds extra flexural reinforcement requirements.
For reinforced concrete design, most design codes require that reinforcement be fully developed at least D past the point where it is required. This is to satisfy the logic of the truss analogy for shear. By normal strength calculation you will need less reinforcement at a point with lower moment D from the point where you are doing the calculations in the direction of reducing moment (top or bottom). But the code requires that the reinforcement supplied at D away is the same as that required at the point. The extra amount RAPT says flexural reinforcement required to satisfy shear.
The actual requirement is actually that the tension force REQUIRED at a point be supplied for a distance D past that point, not the amount of reinforcement supplied. So if you do not require all of the reinforcement supplied at a point, then you only have to extend the amount required at that point by D. Codes have simplified this to simply save to extend all of the reinforcement D past the point.
This distinction between reinforcement and its tension force is important when you look at PT as you obviously cannot extend the PT cable past the point where it terminates. But the requirement still applies to PT. So if a PT tendon is fully required at the point just before it terminates, the force supplied by that tendon at Ultimate must be replaced with normal reinforcement, fully developed back past the tendon and fully developed at least D past that point. If only 50% of the tendon capacity is being used, then 50% of the tension force needs to be replaced.
The only design code that explains this fully for all members Eurocode. The latest Australian commentary also has the same explanation and the next Australian code will be changed to define the requirements properly for both RC and PT members. RAPT follows the Eurocode logic on this for all codes for RC and PT members as none of the other codes explain how it should be treated for PT members and some don't explain it at all.