Trevitest, Sesitest, ValveCheck etc., they are all brand and trade names of manufacturers in-line safety relief valve in-situ test devices. basically the principal between them is the same. In addition to my previous comments on this thread regarding blowdown, I felt it apt to add a few further comments specifically to make users aware of such devices usage. I am not renouncing or promoting the method, but making some observations as an ex SRV manufacturing guy.
* Some users are led to test their newly acquired SRV's prior to initial installation, since they are informed that the new SRV is at a factory setting and correct (OK a few users bench test first). However, with the result obtained with the in-situ device, they calculate back what the pressure area is on the seats of the SRV (Sometimes defined as the area between the outer and inner lapped nozzle seat). The reason for this is because a) They have not had the the areas provided by the SRV vendor (note these areas should be as actual measured and can be sometimes put on manufacturers test certification if requested, and b) require the areas calculated for future on system. in-situ test.
However, in doing this, and sometimes with less than 75 % of set pressure in the inlet of the SRV, the user runs a real risk of damaging the spindle by stretching (this is also why ASME states not to use a lifting lever at less than 75 % set pressure). Result, distorted seating, wrong set pressure etc. Since the user wishes to save time and money, the future testing now carried out without any maintenance, may well be providing in accurate results with the user thinking he had a good accurate initial test.
* The test will never indicate to the user the condition of the critical internal parts (disc, guide, spindle) which must be sound to ensure a proper full lift during a real overpressure excursion.
* The lack of an extended threaded spindle to allow device attachment is not a regular feature on all SRV's. It is known some users have drilled and tapped spindles on an assembled SRV damaging the seats and other parts.
+ And finally, only the point of set pressure is tested, not the lift or blowdown.
Per ISO, only the term Safety Valve is used regardless of application or design.