This inquiry is looking for opinions on safe maintenance access for Safety Relief Valves.
Safety Relief Valve maintenance access has been primarily dictated by the operators design scope. These can be very minimal in description and typically refer to API. API only states that maintenance access should be easily accessed. Not much direction here.
Preparing a more descriptive definition in an effort to improve maintenance access and safety, standardize design layout principles, reduce fabrication and construction costs.
People will argue that safe maintenance access can be achieved off a scaffolding platform, and new designs are being done this way with that philosophy (valve 7 to 10 feet above platform). However is this practical and economical for a 20 to 40 year design plant, not to mention the access mess scaffolding creates for the operators and the increased safety hazard they can create. Do I want to force the operators to live in that environment for the life of the plant?
Considering all design concepts are directed by project scope requirements, defining a requirement for PSV access clarifies the requirements at the front end for structures access requirements.
The following is my minimum project scope description. Please comment opinions and points of view.
Safety Relief Valve Access
- Safety Relief Valves are category 1 access valves (this means easily accessible).
- Valve shall be located at a convenient work height for maintenance removal.
- Access platform for PSV shall be a permanent design.
- Large diameter piping will require the design of an independent platform around the PSV that allows for proper maintenance removal access.
- Platforms shall be accessed by ladder or stair.
- Isolation block valves for PSV do not need permanent access platforms (however nice to have), but must be accessible by manual and mobile methods.
Safety Relief Valve maintenance access has been primarily dictated by the operators design scope. These can be very minimal in description and typically refer to API. API only states that maintenance access should be easily accessed. Not much direction here.
Preparing a more descriptive definition in an effort to improve maintenance access and safety, standardize design layout principles, reduce fabrication and construction costs.
People will argue that safe maintenance access can be achieved off a scaffolding platform, and new designs are being done this way with that philosophy (valve 7 to 10 feet above platform). However is this practical and economical for a 20 to 40 year design plant, not to mention the access mess scaffolding creates for the operators and the increased safety hazard they can create. Do I want to force the operators to live in that environment for the life of the plant?
Considering all design concepts are directed by project scope requirements, defining a requirement for PSV access clarifies the requirements at the front end for structures access requirements.
The following is my minimum project scope description. Please comment opinions and points of view.
Safety Relief Valve Access
- Safety Relief Valves are category 1 access valves (this means easily accessible).
- Valve shall be located at a convenient work height for maintenance removal.
- Access platform for PSV shall be a permanent design.
- Large diameter piping will require the design of an independent platform around the PSV that allows for proper maintenance removal access.
- Platforms shall be accessed by ladder or stair.
- Isolation block valves for PSV do not need permanent access platforms (however nice to have), but must be accessible by manual and mobile methods.